Question thread · 6 questions
Further to the commitment in its Programme for Government to “put in place more stringent fire safety provisions for external wall cladding systems”, what plans it has to stop the alternative route of (a) desktop studie…
Started with S5W-25418 on 19 Sep 2019; latest 9 Oct 2019. Each later question says it follows up an earlier answer.
The thread, in order
Each answer’s opening lines; open a question for the full text-
To ask the Scottish Government, further to the commitment in its Programme for Government to “put in place more stringent fire safety provisions for external wall cladding systems”, what plans it has to stop the alternative route of (a) desktop studies and (b) BS 84814, which allows combustible materials onto the outside of buildings, and when it will release further details of its plans.
Kevin Stewart, 30 Sep 2019: More stringent fire safety provisions for external wall cladding systems were developed from the recommendations of the Building Standards Fire Safety Review Panel. Revised Technical Handbooks were published on 12 July 2019 and apply from 1st October 2019. Provision of external wall cladding systems with a fire classi… -
Whether it will clarify if the requirement for external wall cladding systems on buildings with a storey at more than 11 metres above ground level to have a fire classification of either A1 (non-combustible) or A2 (will not contribute to the fire spread) can be circumvented using the alternative BS 8414 large-scale fire test, which permits combustible materials on to the outside of buildings.
Kevin Stewart, 29 Oct 2019: The BS 8414 large scale fire test is one of the most robust fire tests used for external wall cladding systems in the world. The test has been cited in building regulations since 1 May 2005 as a means of compliance with mandatory standard 2.7 which requires the spread of fire on the external walls of a building to be … -
And in light of a range of industry experts who have reportedly criticised the BS 8414 large-scale fire test, including expert witnesses to the Grenfell Tower Inquiry, which has led to an ongoing review of the standard, and the European Commission’s rejection of BS 8414 as a harmonised test standard, for what reason it continues to permit this route to using combustible materials on the façades of high-rise and high…
Kevin Stewart, 29 Oct 2019: The Scottish Government will consider the recommendations of the Grenfell Tower Inquiry when they are published. National and International members of the Building Standards Fire Safety Review Panel fully supported the continued use of the BS 8414 large scale façade test. It is incorrect to say that the European Commi… -
Whether it will clarify if the requirement for external wall cladding systems on assembly and entertainment buildings and to hospitals and residential care buildings, regardless of height, to have a fire classification of either A1 (non-combustible) or A2 (will not contribute to the fire spread) can be circumvented using the alternative BS 8414 large-scale fire test, which permits combustible materials on to the out…
Kevin Stewart, 29 Oct 2019: I refer the Member to the answer to question S5W-25755 on 29 October 2019. All answers to written parliamentary questions are available on the Parliament's website, the search facility for which can be found at: http://www.parliament.scot/parliamentarybusiness/28877.aspx -
Whether it will confirm that the alternative BS 8414 test is a large-scale fire test, rather than a full-scale fire test.
Kevin Stewart, 29 Oct 2019: BS 8414 is a large-scale test of a full-scale cladding system though neither of the terms ‘large-scale’ or ‘full-scale’ are used in the document itself. BS 8414 tests the vertical fire spread performance of an 8 metre tall external wall cladding system. The system includes sheeting rails, fixings, cavities, cavity bar… -
Whether it will confirm that desktop studies, which use data from previous BS 8414 large-scale tests to extrapolate how an external system would perform if it were tested, are supported and recognised as a route to compliance with Scottish building regulations via legally permitted alternative guidance.
Kevin Stewart, 29 Oct 2019: The term “desktop study” has commonly been used to describe an assessment in lieu of a fire test. Desktop studies have never been recognised or supported as a route to compliance with Scottish building regulations. Direct application rules for cladding systems which has been subjected to a single or multiple BS 8414 f…
How this thread is put together
- Follow-up
- A question whose text says it is “further to the answer to question …” (or reply, response, or asks for a “substantive answer” to an earlier question). The question it names is its parent.
- Several citations
- When a question cites more than one earlier question, the most recent one we hold is used as the parent; the others are listed as “also cites”.
- Thread