The question

To ask the Scottish Government, further to the answer to question S5W-25418 by Kevin Stewart on 30 September 2019, whether it will clarify if the requirement for external wall cladding systems on buildings with a storey at more than 11 metres above ground level to have a fire classification of either A1 (non-combustible) or A2 (will not contribute to the fire spread) can be circumvented using the alternative BS 8414 large-scale fire test, which permits combustible materials on to the outside of buildings.

The answer

Answered by Kevin Stewart on 29 Oct 2019 · 20 days after it was lodged, on time

The BS 8414 large scale fire test is one of the most robust fire tests used for external wall cladding systems in the world. The test has been cited in building regulations since 1 May 2005 as a means of compliance with mandatory standard 2.7 which requires the spread of fire on the external walls of a building to be inhibited.